请问electrician’s report里面最重要严重的是哪个项目? 我还没有exchange contract, 希望看看是否有必要 negotiate offer.
因为会重新装修所以我猜不需要马上修复所有的,e.g.8)bathroom ceiling light not IP65 rated反正我们会更换bathroom light
但哪一个比较严重ne?我应该问卖家降价还是请他去修理?
感觉或许13比较严重? 需要多少费用ne?
Item No Observations Classification
Code
Further
Investigation
Required
1 Absence of Isolator switch for supply cable from electricity meter to the consumer unit. ( cable is longer than 3 metres from electricity meter ) C3 N/A
2 Absence of additional protection by 30mA rcd for all sockets outlet. C3 N/A
3 Absence of additional protection by 30mA rcd for Bathroom lights. C2 N/A
4 Absence of cross bonding of pipe work at the kitchen sink. C3 N/A
5 Absence of cross bonding of pipe work at the bathroom basin. C2 N/A
6 Absence of earth fly leads at the metal light switches hallway and kitchen. C2 N/A
7 3 circuits fed form the same mcb circuit number 5. C3 N/A
8 Bathroom ceiling light not IP65 rated however located above 2.25m from the floor level. C3 N/A
9 Bathroom wall light not IP65 rated. C2 N/A
10 Bathroom extractor fan not functional. C3 N/A
11 Hallway ceiling lights not installed properly. C2 N/A
12 Smoke alrm not located within the specified requirements. C3 N/A
13 There is no continuity of ring main circuit L to L, N to N, E to E. C2 Yes