Villant 637+Villant cylinder,今天早上发现图片上黑色胶那个part湿湿的,地上有一滩水。这是咋回事啊?



西北老兄正放假,估计不多久就回来。 {:5_134:}

我家的这个连接处也有轻微的漏水。。。也不知道是啥情况。。。

Water being discharged through the tundish. A tundish is a visual device to show when water is passing through to highlight the fact there is a possible fault with a safety device on the unvented cylinder. There are a number of reasons that water could be discharging through the tundish. Valves which could cause this are the pressure & temperature relief valve; the expansion relief valve the pressure reducing valve or even the expansion vessel. If hot water is being discharged via the tundish this would normally point to the pressure & temperature relief valve. If it is cold water then you would need to check the pressure reducer & expansion relief valve (normally combined on an unvented hot water cylinder) or it could mean that the pressure in the expansion vessel is not holding.

我家是暖气开的多,漏的就厉害些,最近天暖和了,就基本不漏了,你也是这样吗?

我家冬天暖气就没停过,也一直没见漏,就最近漏了一次

水罐外面的的白色膨胀球 (expansion vessel),需要打气了。

一般3年左右需要打一次气。

谢谢您回复,但我们家的是去年10月新装的,刚装完那时漏过2次,之后就没再漏了,这最近又漏了一次。

多谢告知,我去查下如何打气,感谢

现在有些系统不用expansion vessel,只是两个限压阀,和一个减压阀。这种安装有什么说法吗?谢谢大哥

这个漏斗经常漏水的话,需要找人修理,也可能是压力和温度的混合泄放阀门有问题,但是更过的还是膨胀球的问题。

只有一个厂家的还在用这样内置膨胀球的技术,Heatrae Sadia 的 Megaflo,一个我到处抨击的失败技术。

但是话说回来了,就我这样的几个会维修的人看不上这个内置技术。Heatrae Sadia 而这是个大公司,设计工程师可能有10多个人,每个人都是工科毕业,假设我去应聘他们的职位的话,可能都拿不到他们的任何一个位置。也就是说,他们也不是笨蛋。

但是为什么他们不跟别的厂家一样,用外置膨胀球技术,而自己发明了所谓的内置 internal air gap。我在实践中,认为这个 internal air gas 很短时间内就失效。所以厂家贴出了一个不干胶的 stick,告诉用户,隔几个月自己 re generate 一下这个 air gap.

都成笑话了!

有人说水煲上调温度的那个太高了,结果我从60左右调到50,今天又漏了一次水,不过水量少过以前很多,您觉得这之间有关系吗?您说的打气,自己能弄得了吗?还是要专业的人过来打气?

跟水包预设温度关系不大。还是膨胀球,或者 T & P valve 坏了。

请问打气自己能打吗?还是要专业人员过来打

看你平时的动手能力了,分人。

如果你是理工毕业的,也能买个给汽车轮胎打气的人工泵的话,你可以试试。

其实你们家多久漏一次水啊

谢谢师父,我能不能理解成用这几个限压阀和减压阀也能代替这个球的作用吗?他们的工作原理都是一样的吧?

没有不用 expansion vessel 的,只不过我上面说的那款,把膨胀球的功能放到水包里了,你看不见。

估计还是要找专业的人来看一下

我们家也不是总漏,几个月里面见过三次地下湿了,你们家呢